Developer Portal Community

    We are moving! We are currently migrating our community to the new Bosch Connected Industry Online Portal. The community will be available latest in the new year again, until then it will be in read-only mode. Click here for more information.

    cancel
    Showing results for 
    Search instead for 
    Did you mean: 
    SOLVED

    Run HMI Locally

    Run HMI Locally

    JosueGB7
    Occasional Visitor

    Hello all,

    I have this issue every time when I try to run HMI locally and then the locally HMI cannot conect to the PLC.

    -------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

    VisiWinNET Compact V6.5.5.25 System Log

    > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > >
    Memory Report
    Global: Max. Progr.: 2097151.99902344 kB, used percent: 38 %
    Application: Max. total: 2097024 kB, used: 266504 kB, free: 1830520 kB, managed: 686 kB
    Info in headers: (A:free in kB M:managed in kB)

    2022-03-31 13:36:23 (A:1830628kB M:638kB) [Info] <Project Handler>
    Starting project OpCon.HMI.Modulo! Project file: C:\Bosch\Proyectos\UpgradeEKP\01_DevelopmentSoftware\XXXX.prj\XXXX.CX2020\HMImodulo\OpCon.HMI.Modulo.vwn


    2022-03-31 13:36:23 (A:1824776kB M:9696kB) [Info] <Data Access and OPC>
    Licensed for Robert Bosch GmbH.
    23 internal and 6317 external items defined in 1 channels.
    License contains 500000 external and 500000 internal items.

    2022-03-31 13:36:23 (A:1824264kB M:9712kB) [Info] <Language Switching>
    System started!

    2022-03-31 13:36:23 (A:1824224kB M:9720kB) [Info] <Data Access and OPC>
    The driver Beckhoff will be loaded from C:\Program Files (x86)\Common Files\Inosoft\VisiWinNET 2005\\Drivers\VisiWinNET\Beckhoff\2.0\VisiWinNET.Beckhoff.Drv.dll.

    2022-03-31 13:36:24 (A:1815240kB M:9764kB) [Info] <Driver Beckhoff at Channel Ch1>
    System (Version: 2.0.5.31) started!

    2022-03-31 13:36:24 (A:1813680kB M:9367kB) [Info] <Data Access and OPC>
    System started!

    2022-03-31 13:36:24 (A:1812272kB M:9391kB) [Info] <Logging>
    System started!

    2022-03-31 13:36:24 (A:1831400kB M:9407kB) [Info] <Alarming System>
    System started!

    2022-03-31 13:36:24 (A:1831400kB M:9415kB) [Info] <Recipe System>
    System started!

    2022-03-31 13:36:24 (A:1831400kB M:9431kB) [Info] <User Management>
    System started!

    2022-03-31 13:36:24 (A:1830120kB M:9447kB) [Info] <Historical Trending>
    System started!

    2022-03-31 13:36:24 (A:1797292kB M:9486kB) [Error] <Driver Beckhoff at Channel Ch1>
    Execption <Ads-Error 0x7 : Taget machine could not be found.> in line 1 while connecting the PLC [ADSNotification]

    2022-03-31 13:36:24 (A:1797292kB M:9494kB) [Info] <Data Access and OPC>
    Internal driver communication started.

    2022-03-31 13:44:52 (A:1782684kB M:10605kB) [Info] <Project Handler>
    Successfully initialized project!

    + + + + + + + + + + + + + + + + + +

    -------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

    Could anybody help me with this please?

    3 REPLIES 3

    Thorsten_Brach
    New Contributor

    Did you check the AMS Net ID and ADS Port in your configuration ?

    Thorsten_Brach_1-1648793534488.png

    The configuration must match to your PLC target system :

    Thorsten_Brach_2-1648793586695.png

    For a local running PLC - you can use 127.0.0.1.1.1 as  AMS Net ID.

    You can find the used ADS Port in your PLC project :

    Thorsten_Brach_4-1648794047585.png

    If you want to connect to a PLC on a remote IPC,
    you also must have a valid route to the target system :

    Thorsten_Brach_3-1648793944563.png

     

     

     

     

    SteffenR-
    Community Moderator
    Community Moderator

    If you have a real hardware PLC and want to run the HMI locally on your laptop you must configure the target systems like this:
    SteffenR_0-1648802044076.png

    If you start the HMI next to the PLC the HMI expects to find the PLC on the same system (localhost):
    SteffenR_1-1648802093428.png

     

    Now its working, thanks for the support.

    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist