We are moving! We are currently migrating our community to the new Bosch Connected Industry Online Portal. The community will be available latest in the new year again, until then it will be in read-only mode. Click here for more information.
10-27-2023 08:51 AM
Goodmorning,
I have a problem with a CX Nexeed Control Plus (Windows 10) used for some comunication with an external bench. During the automatic cycle, in random mode, the CX stop the comunication with the external bench and on the HMI is displayed the attached error. At this time all the app services are stopped and the only way for comunicate again with the CX is to restart it from windows functionality (twincat restart isn't working).
Thanks for the help!
Regards.
Solved! Go to Solution.
10-27-2023 09:19 AM
I can’t imagine this popup causing the error.
In the HMI you can see, that somehow all connections are interrupted - maybe there is a problem with the network.
Probably this message pops up, because this OpconDesktopInfo.vbs script also reads information from the network settings and displays it on the desktop.
As you mentioned, you can not restart the TwinCat Runtime,
so it would be interesting to know the status of the Runtime - maybe you can take a screenshot with open Taskbar,
so that the Twincat runtime icon is to see...
10-27-2023 09:43 AM
have you the newest version of DataSetAccess service.
10-27-2023 10:17 AM
10-27-2023 10:32 AM
The DataSetAccess memory leak occurs when there is an additional outdated configuration for DataSetAccess on the target system. Please check if there is more than one subfolder underneath C:\OpconApp\DataSetAccess\Config. If so, please check which one is the valid one (compare with DataSetAccess folder in CpStudio project) and delete the other one(s).