How old is the image that you using on your PLC?
Please install the TwinCat TCP/IP server from new or install image from new.
-------------------------------------------------------------------------------------
Install TCP/IP Server
1. Log on as OpconAdmin
2. Uninstall the current TCP/IP server
3. Restart PLC
4. Instalation files for the TCP/IP server you find on our image stick or direct on the PLC(C:\TwinCat.SetingFiles\) if you using one of the newer image version.
5. (Very important)Right click on TF6310-TCP-IP.exe and run installation as "Administrator".
6. After install TCP/IP server, restart PLC and Log on as OpconUser
04-22-2022 02:38 AM
I re-installed the system directly, thank you
08-17-2022 03:44 PM
Hi friend,
In the current high version of OES, the color of this alarm is directly displayed as a red alarm.
Solution: Reinstall TF6310, But it should be noted that it also requires a license.
08-18-2022 01:37 PM
If you buy systems from BCI, you have the license.