Failure description:
When the working process ceased by operator (such as switch to manual mode), it has possiblity that the CCS library instant record the last processing result. When a new part placed into station, the CCS will start and stop the process in less than 1s and exprot the OK result.
Temporary solution:
The operator needs to reset the PLC.'
Related info.:
This same failure has happened on CCS test station in 3x ECU lines in BHSS.
Line4: V2.0.14.0, the MAE supplier is XENON;
Line6&7: V2.0.12.0, the MAE supplier is BMG.
Solved! Go to Solution.
07-10-2023 10:50 AM
Lib not save any data internal.
After mode change the lib start cancel and delte the internal buffer.
What i think.
When the command is aborted on the controller, no abort on the CCS controller.
So when you start a new command, I think that the CCS sends an old telegram.
For reset CCS site, our object have the comand RESET. But this RESET must programing on CCS site to.