We are still working on migrating to the new Bosch Connected Industry Online Portal. Stay tuned! Click here for the latest updates.
04-19-2023 10:47 AM
Hello,
One question I have is how to use the enable button with dummy connector. according to the instruction of periheral, the step are
1.inserted the dummy plug to robot controller
2.configured the iomap.cfx file
the question are:
1. should I change the dummy connector? I mean I need to connect enable button to the dummy connector?
2.or follow 'safety wiring via Ethernet', actually I am not understanding how the function is work
thank you
Solved! Go to Solution.
05-16-2023 03:49 PM - edited 05-16-2023 03:50 PM
If you want to jog the robot with safe-limited-speed while the safetydoor is overrided and the enable button is pressed,
then the Robot mode must be set to manual [T1] - ( The stäubli accept UniValPlc commands also in Mode T1 )
If you have a closed cell without any safetydoor, then the robot can remain always in Remote .
05-18-2023 02:38 AM
thank you very much~
if I do not set to T1 mode, what is then happened? the robot cannot be jog by PLC from system side? or just only considering the safety, so we must configure like that? if I need to set some configuration in the robot side? thank you
09-29-2023 02:24 AM
thank you for your support ^^ the robot is working well with safety function now