We are still working on migrating to the new Bosch Connected Industry Online Portal. Stay tuned! Click here for the latest updates.
06-19-2024 03:49 PM
Hello Community
I make some tests with the NxConsumptionAddon. I connected the NexeedIfmSensor to the NxConsumptionAddon. If I use the ConsumptionCalcMode "S0COUNT", the ConsumptionValue was still present after a PLC reset cold.
If I use the ConsumptionCalcMode "ANALOGCOUNT", the ConsumptionValue = 0, after reset cold.
I think the consumption value is stored persistent in the NexeedIfmSensor object. During initialisation after restart PLC, somthing went wrong.
Solved! Go to Solution.
07-02-2024 10:34 AM
@BCI
I have a testproject and I can show you this behavior.
07-10-2024 01:15 PM
This seems to be a bug in the underlying library AtmoDiscreteControlSystemsIntegrated.lib.
I will create a helpdesk ticket to solve the problem.