08-01-2022 12:14 PM
I used OES4.5 before, download the program after configuration, the HMI will have an alarm display,
But now I changed to OES4.11 and there is no alarm display, I also added Event LIST.
Solved! Go to Solution.
08-01-2022 05:56 PM
Sorry, but in the last screenshot I can see that my question does not apply to your project. This cannot be the reason if the project only has one ModeHandler.
Do you get any errors when starting the HMI?
08-02-2022 03:44 AM - edited 08-02-2022 04:08 AM
I read the log file and the cause of the error is that the variable is not configured,(No symbol information for variable Station.EventList.Entry[1].Event.InstanceId line:1)
But OES4.5 is configured as BaseMov standard, If the sensor action is wrong, HMI will display an alarm.
The same configuration doesn't show up in OES4.11, I find it weird!
Because the forum attachment does not support txt format file upload, so I cut a small part of the picture
08-02-2022 05:05 AM
Hello nexidator,
After I recompiled and downloaded the programs of TwinCAT3 and OES, the alarm appeared, and I don't know the reason.
In addition, I have another OES program, when I check the PLC project in OES, there is an error, and I can't find the reason.
please help me, thanks
08-02-2022 09:12 AM - edited 08-02-2022 09:15 AM
08-02-2022 09:46 AM
hello SteffenR-:
My problematic project used TwinCAT3 4022.27 and OES version 4.5. There was a big problem between them,
so I later used OES4.11 and TwinCAT3 4022.27 without any problem.
Thanks for your guidance.