Hello,
Does anybody know if there's a variant to disable and enable automatically the modules on the EtherCat, for TwinCat3 Build 4020?
I saw that starting with build 4024, there is a posibility to use the Project variant, and I was thinking maybe there is something that can be used also on this older build.
Thank you!
09-08-2023 07:18 AM
Checkout the Hot Connect Group functionality.
https://infosys.beckhoff.com/content/1033/ethercatsystem/2469078667.html
This is a good way that the bus is running, when the modules are not there.
The more complex thing is to adjust the EtherCAT slaves in the OpconEcMasterBase. You have to disable the StateChecks that your master tells "CheckedBusOk"
09-22-2023 05:38 PM
"The more complex thing" mentioned by @FlorianNisch is described in the Application Guideline V1.3 (or newer):
There is also a forum post that addresses this topic already: