Is there a way that I can have more Sub Chains please? If I add many Sub Chains (e.g. to Station Mode Handler) I get the error shown in the photo below.
What are the maximum Sub-Chain limits please? e.g.
- 10 Sub Chains per Mode Handler ?
- 10 Sub Chains per Command Handler?
Many thanks! 😊
Solved! Go to Solution.
06-23-2022 09:00 AM
you can change it in OpconBaseConfig in OpconBase library, the default value is 10, after change it, you should do "Clean Solution" -> "Rebulid Solution" and login to make it effective.
06-23-2022 09:01 AM - edited 06-23-2022 09:13 AM
Some libraries have constants that can be changed in the PLC application ("library parameters"). This feature prevents that the developer must build a new library version just to increase an array/string size.
You may change the constants in the PLC library manager (double click on "References" or any referenced library/placeholder):
Very important:
Additional note:
If you have started your project with an OpconBase version less than 1.0.7.0, you must remove this placeholder/library from your project and export again (using at least OpconBase V1.0.7.0).
Useful examples:
Some constants may affect variables used in the HMI:
06-24-2022 01:19 AM
Thanks Steffen! 😊