We are using Event Recorder App V1.5.5 on a machine. I noticed that whenever I set an event with text that contains a place holder {0} and clear the event in the next step. I always get minimal 2 entrys in the event recorder. I also tried waiting 2 seconds between set and clear event but i still get minimal 2 event in the event recorder. The only way to prevent it, is to remove the place holder {0} then everything works fine, but I need that place holder for the variable data. Is there some way to prevent this double entry and use the place holder?
02-28-2023 09:22 AM
This looks really weird, but actually I am quite sure there is no general problem with event texts using {0}.
(Alternatively, you can contact our helpdesk so we can give you directions how you can send us your project for analysing the behavior.)
03-01-2023 08:43 AM - last edited on 03-01-2023 08:49 AM by nexidator
Event runtime version seems to be V 1.5.5.4
The even recorder app seems to be V1.5.5
step N246:
// Info Message with current holder nr: if holder was changes
IF ( YZAxis.Unit.OutCmd.HolderNo = _holderNoMemory )
THEN
_retVal := OK;
ELSE
IF (_eventPlc = 0)
THEN
_eventPlc := SetEvent(OpconEventClass.INFO, INFO_HOLDER_NR, INT_TO_STRING(YZAxis.Unit.OutCmd.HolderNo), Lock:= FALSE);
_holderNoMemory := YZAxis.Unit.OutCmd.HolderNo;
_retVal := OpconSetTimeout(_waitTimeEvent,_waitTimer);
ELSE
_retVal := RUNNING;
END_IF
END_IF
step N247:
// Clear holder Nr info message
IF (_eventPlc <> 0)
THEN
IF ( OpconCheckTimeout(_waitTimer) = OK )
THEN
ClearEvent(OpconEventClass.INFO, _eventPlc);
_eventPlc := 0;
_retVal := OK;
ELSE
_retVal := RUNNING;
END_IF
ELSE
_retVal := OK;
END_IF
03-01-2023 09:43 AM
Thanks for posting your code. As expected, it doesn't look like it can be the reason for the duplicate entry. (I am not sure if "ELSE _retVal:=RUNNING" in the first step makes much sense, but I don't see how it could run into this line anyway.)
One thing I forget to ask: Does the event appear twice in the HMI as well? I guess not, and otherwise this must really be a problem of the EventRecorder service.
Can you try if it helps to update to the latest version of the EventRecorder service (V1.5.9)? I have seen in the change history that some bugs have been fixed since the version you are using.
03-02-2023 01:43 PM
I Installed the new version of eventrecorder service V1.5.9.1 and event recorder app V1.5.7.7 , export, deployed including std. but the result stays the same.
On the HMI I only see one Message.