11-09-2023 02:40 PM
Hello,
Whenever I configure the CG mode in CPS, after download and cold restart the PLC stops with an exception error. Unfortunately, I am unable to determine the exact cause as it refers to an object within. I believe I might have misconfigured some parameters. I have been going through the documentation, but it is still unclear where I might be going wrong.
If i delete everithing from CPS and Twincat I'm able to recover PLC to run mode.
Any help would be appreciated.
Thank you in advance for your help.
Csaba
Solved! Go to Solution.
11-09-2023 03:11 PM
Please provide a screenshot of the call stack:
11-09-2023 03:41 PM
11-09-2023 04:18 PM
Did you add at least one CgProbe add-on?
See documentation:
If you have added a probe, please check the online value of the local variables _probeCounter and _selectedIndex in case of a Page Fault Exception.
11-10-2023 10:14 AM
Thank you for your help.
It looks like the only step I missed was the first one.
By any chance is there any sample project for this mode for better understandin?