I'm testing the new IO Link Master features released recently and I am encountering some issues. I'm attempting to use the IO-Link port of the BIS V-6110 to support a Balluff Smart Light (V2.1.3.0)
1) The Export causes an Error in OES V4.11. PeripheralUnitDrop.TypeId doesn't exist in version 4.11 of OES. The Export works correctly using CPS V5.4
Modifying NexeedEcBalluffBisv6110\V2.0\Export\StartupParams.otd to use
child.DeviceTypeId.Equals("16777448_397578|4610")
instead of
child.TypeId.Equals("A46802C5-013E-11E1-8619-000423132FC8")
allows 4.11 to export.
2) I'm getting the following errors when building the TwinCAT project.
3) I also just noticed that both documentation links in NexeedEcBalluffBisv.ood link to Documentation\NexeedEcBalluffBisV6110_TechnicalManual_DE.chm Looks like this was an issue in V1.1 as well.
Solved! Go to Solution.
04-03-2023 12:14 PM
Thank you for the detailed description. The issues described have been fixed and the updated objects will be made available on our dowloand server.
04-03-2023 01:36 PM
Thanks for the quick fix! I've downloaded and tested the updated objects and everything seems to be working as expected. Thanks again!